I believe I haven't come across this yet, but how do you apply Table 220.55 to size a feeder / service having a range that is over 12kw? What demand factor can you use? Column A is only up to a 3.5kw rating, column B is up to 8.75kw, and column C is up to 12kw.

I'm assuming you take it at 100%, since it's KW rating is so high?
 
See Note 1: Your answer is based on Column C with that number increased by 5% for each kilowatt or major fraction of over 12.
Example D6 in Annex D illustrates the procedure.
 
Last edited:
See Note 1: Your answer is based on Column C with that number increased by 5% for each kilowatt or major fraction of over 12.
Example D6 in Annex D illustrates the procedure.
Oh I see it! ok that's pretty clear... just had to go to the notes!! Thanks.
 