I have a project that consists of 3 residential buildings, each with 30 apartments. All 3 buildings are powered by the same substation (1500 KVA). The utility point of connection is at a switchgear (13.2 KV). I run a service conductor from the switchgear to the substation. From the substation I run an individual feeder to each building. In order to obtain the substation size or the service conductor size, using the optional calculation method, can I use the total number of apartments (90) for my demand factor or do I have to take each individual feeder load per building (demand factor for 30 apartments) and add that load to obtain my total load? If I use 90 apartments the demand factor is 0.23 based on Table 220.84. If I use 30 apartments the demand factor is 0.33. Please let me know your opinion about this subject