Hi all
Last night, one of my students asked me a question about the above-referenced table in Article 250. He was confused by the boldface heading the right column which reads: Size of Grounded Conductor or Bonding Jumper (AWG or Kcmil). This is followed by an asterisk which sends one to the bottom of the table notes and it reads: For the purposes of this table, the term bonding jumper refers to main bonding jumpers, system bonding jumpers, and supply side bonding jumpers.
His question was why does it say Grounded Conductor and not just Bonding Jumper. I told him I thought it was because this table refers to supply side conductors and that there are times a utility will size a grounded conductor differently than one might if using article 220. That's just a guess. I promised I would post the question on the forum.
Anyone care to weigh in?
Thanks
Last night, one of my students asked me a question about the above-referenced table in Article 250. He was confused by the boldface heading the right column which reads: Size of Grounded Conductor or Bonding Jumper (AWG or Kcmil). This is followed by an asterisk which sends one to the bottom of the table notes and it reads: For the purposes of this table, the term bonding jumper refers to main bonding jumpers, system bonding jumpers, and supply side bonding jumpers.
His question was why does it say Grounded Conductor and not just Bonding Jumper. I told him I thought it was because this table refers to supply side conductors and that there are times a utility will size a grounded conductor differently than one might if using article 220. That's just a guess. I promised I would post the question on the forum.
Anyone care to weigh in?
Thanks