Hi,
I have watched Mike Holt's YouTube video on table 250.102(C) but I was still looking for some clarification.
I have a 2500 KVA transformer with 34.5 KV- 480/277, and #3/0 grounding electrode conductor. On the secondary side of the transformer (Load side) I have 250 feet of feeder and the feeder information is as follow:
8 sets of 4 wire (3 phase, 1 neutral) #600 KCMIL, with 1 #600 kCMIL GND in 4" conduit.
Therefore, in each of the 8 set conduits, I have 5 wires total, 3 phase, 1 neutral, and 1 ground.
I was wondering if that #600 KCMIL ground conductor in each set is accurate? According to note 1 of table 250.102 (C) I have"
8 x 600 = 4800 KCMIL
4800 KCMIL x .125 = 600 KCMIL
Is that the ground wire that needs to be routed in each conduit (set), or is that what the overall size should be and I need to split that up into 8 smaller wires?
I have watched Mike Holt's YouTube video on table 250.102(C) but I was still looking for some clarification.
I have a 2500 KVA transformer with 34.5 KV- 480/277, and #3/0 grounding electrode conductor. On the secondary side of the transformer (Load side) I have 250 feet of feeder and the feeder information is as follow:
8 sets of 4 wire (3 phase, 1 neutral) #600 KCMIL, with 1 #600 kCMIL GND in 4" conduit.
Therefore, in each of the 8 set conduits, I have 5 wires total, 3 phase, 1 neutral, and 1 ground.
I was wondering if that #600 KCMIL ground conductor in each set is accurate? According to note 1 of table 250.102 (C) I have"
8 x 600 = 4800 KCMIL
4800 KCMIL x .125 = 600 KCMIL
Is that the ground wire that needs to be routed in each conduit (set), or is that what the overall size should be and I need to split that up into 8 smaller wires?