Table 300.5 Burial depths - Residential?

Status
Not open for further replies.
What is the definition of Residential? Table 300.5, Column 4, covers Residential Branch circuits 120V or less and with GFCI protection with OCP 20A max. I am unable to find the definition in the NEC. Thanks
 
Does a 6 story 36 unit Time Share condo fall under Residential? The reason I ask, we are having some 120V site lighting installed and they are going 12" deep and putting it on a GFCI as per column 4. I always thought of Residential as a House, just looking for clarification.
 
Honestly not sure how condos in FL would be classed. There are several members here from FL who can answer your question. Personally, I'd check with the AHJ, or just dig the trenches deeper.
 
Article 100 "Dwelling unit" - "A single unit, providing complete and independant living facilities for one or more persons, including permanent provisions for living, sleeping, cooking, and sanitation."
A dwelling unit is considered residential so you would use Column 4.
 
I would say that a 100 story apartment building could be called a residential building.
 
Does a 6 story 36 unit Time Share condo fall under Residential? The reason I ask, we are having some 120V site lighting installed and they are going 12" deep and putting it on a GFCI as per column 4. I always thought of Residential as a House, just looking for clarification.

You raise a good question and the code is ambiguous on the matter.

As to someone who suggested looking at zoning, we have a state law in Florida that says you can't use zoning to enforce building codes and you can't use building codes to enforce zoning.

I'm going to be of the opinion that you are ok at 12" burial. Reason being is that the word "residential" as used in building codes, while not specifically defined as a stand-alone word, is commonly used to include residential 1&2 family dwellings, transient residential occupancies (hotels, motels, timeshares) and other forms of residential occupancies. Additionally, that same table does use the language "1 & 2 Family Dwelling" so they must mean something different with their use of the word "Residential".

But if I were installing it, I'd put it at 24". There are very likely commercial uses on the property (front desk, commercial laundry, housekeeping, commercial kitchen, entertainment venues, etc.). It boils down to a risk/ reward matter. What happens if the inspector says it needs to be 24". How effort would it have taken? (you might be in sugar sand and it might be coral). Can you 100% defend your position of 12" if someone gets injured? There's always going to be someone who sees it in a different light. When something is ambiguous I usually lean towards the safer outcome.

I don't think AHJ has cause to fail your installation at 12".
 
What is the definition of Residential? Table 300.5, Column 4, covers Residential Branch circuits 120V or less and with GFCI protection with OCP 20A max. I am unable to find the definition in the NEC. Thanks
YOU do not need to determine if it is residential or not. What does it say on the plans? Most of the multi-family that comes across my desk are mixed. The individual units are done per the IRC (International Residential Code) and the common areas (lobby, courtyards, laundry, parking garage, corridors, etc) are treated as commercial areas and under the NEC.

The electrical section of the IRC is "similar" to the NEC, but the sections are numbered different and is "watered down" in some areas that will leave you scratching your head! :p
 
plans dont mean much if they spec via IRC but the AHJ uses NEC.
call the AHJ and ask. if there is discrepancy between the plans and AHJ, then its an issue for someone else, etc.
 