Everytime I read an low voltage residential landscape installation guide on the internet or from a manufacture, they say you can bury the LV cable about 2 inches under the ground. I can't find any code that allows that.
I looked at NEC 411 for something and it only says NEC 300 methods. When I look at T300.5 Col 5 it talks about control wires being 6" for all locations not specified. However, for all dwelling driveways, parking areas and used only for dwelling related purposes, it shows 18".
Based on what I see, for direct burial cables or conductors it looks like you have to go 18" even it if it lanscape lighting cables. Let me know if there is another code that would change that.