I’m wiring a scale house and I need to get raceways from inside wall of the building to the outside scale area.
I have 3 low voltage raceways and 2 -120/240v raceways.
Looks like since I have no vehicular traffic in the slab I’m going under. I only need to be 4” beneath the bottom of the slab of concrete ?
Also looks like I will need to have schedule 80 sweeps, and expansion couplings emerging from concrete in outside area.
Can I get away with out expansion coupling and sched 80 sweep on raceway coming into the building wall?