Can I assume that a PVC raceway under a commercial driveway is legal if encased in 2" of concrete regardless of burial depth? Assumption based on Note 2.
Nope. You might get away with 12", row 2. IDK, never tried.
Under streets, highways, roads, alleys, driveways, and parking lots
See the row labeled
24" there.
I know the table, I have always been speced at that depth, I am just not sure that if you use that 2" concrete idea if 12" is okay.
What conduit would require encasement in concrete if it is buried? Not talking about over 600V or inside a building.
2. Raceways approved for burial only where concrete encased shall require concrete envelope not less than 50 mm (2 in.) thick.
What conduit would require encasement in concrete if it is buried? Not talking about over 600V or inside a building.
http://www.highlandvalleysupply.com/ProductListing.aspx?ProductCategory=20
It is basically schedule 20 PVC for use in duct banks.
What conduit would require encasement in concrete if it is buried? Not talking about over 600V or inside a building.
I thought that stuff was like true URD and limited to POCO.
from 2012 UL White Book:
RIGID NONMETALLIC CELLULAR CORE SCHEDULE 40 AND SCHEDULE 80 PVC CONDUIT (DZLR) ....
Unless marked for higher temperatures, rigid nonmetallic cellular core PVC conduit is intended for use with conductors and cable rated 75?C or less, including where it is encased in concrete within buildings and where ambient temperature is 50?C or less. Where encased in concrete in trenches outside of buildings, it is suitable for use with conductors and cable rated 90?C or less. ....
RIGID NONMETALLIC PVC CONDUIT (DZYR) ....
Type A, Type EB and Schedule 40 conduit is intended for underground
use under the following conditions, as indicated in the Listing Mark:
Type A ? Installed with its entire length in concrete in any underground location.
Type EB ? Installed with its entire length in concrete in trenches outside of buildings.
Schedule 40 ? Direct burial with or without being encased in concrete. ....
Unless marked for higher temperature, rigid nonmetallic PVC conduit is intended for use with wire rated 75?C or less including where it is encased in concrete within buildings and where ambient temperature is 50?C or less. Where encased in concrete in trenches outside of buildings it is suitable for use with wires rated 90?C or less. ....
RIGID NONMETALLIC HIGH-DENSITY POLYETHYLENE UNDERGROUND CONDUIT (EAZX) ....
Unless marked otherwise, HDPE conduit is intended for use with wire rated 75?C or less, or when directly buried or encased in concrete in trenches outside of buildings, it may be used with wire rated 90?C or less. ....
OK, I will stop trying to answer your question.