Hi,
So Table 300.50, Column 4 has the minimum cover requirements for "Raceways Under Buildings or Exterior Concrete Slabs, 100 mm (4 in.) Minimum Thickness" and it's 4in below 40kV.
Based on my understanding, I need 4" between the top of my conduit and the top surface of the slab. With column 4 specifying the minimum thickness of slab as 4in, then this would mean that my conduit is buried directly below the slab, as a minimum. Is this correct?
Then I read footnote "d", which says "The slab shall extend a minimum of 150 mm (6 in.) beyond the underground installation, and a warning ribbon
or other effective means suitable for the conditions shall be placed above the underground installation. "
Does this mean that I need the slab to extend 6in below the bottom of the conduit?
For example, if installing a 6in conduit (to simplify, let's say it has an OD of 6in), this would mean slab would have a thickness of 16in (4in above conduit + 6in conduit diameter + 6in below conduit)?
Thanks,
Yogi
So Table 300.50, Column 4 has the minimum cover requirements for "Raceways Under Buildings or Exterior Concrete Slabs, 100 mm (4 in.) Minimum Thickness" and it's 4in below 40kV.
Based on my understanding, I need 4" between the top of my conduit and the top surface of the slab. With column 4 specifying the minimum thickness of slab as 4in, then this would mean that my conduit is buried directly below the slab, as a minimum. Is this correct?
Then I read footnote "d", which says "The slab shall extend a minimum of 150 mm (6 in.) beyond the underground installation, and a warning ribbon
or other effective means suitable for the conditions shall be placed above the underground installation. "
Does this mean that I need the slab to extend 6in below the bottom of the conduit?
For example, if installing a 6in conduit (to simplify, let's say it has an OD of 6in), this would mean slab would have a thickness of 16in (4in above conduit + 6in conduit diameter + 6in below conduit)?
Thanks,
Yogi