Table 310.104(E) Cable Insulation

Status
Not open for further replies.
Location
USA
Occupation
Electrical
Can anyone give me an explanation of how duration of line to ground fault is tied to the insulation level (100%,133%, 173%) of the cable? See notes 1,2,3 in NEC 2011/2014 Table 310.104(E). I'm curious how these times were determined and if fault current has anything to do with this duration.

Reason I am asking is if I have a 5kV low-resistance grounded system with a relay that only has instantaneous (ANSI 50G element) where the INST pickup current is set to 20A, do I technically need a timer that opens the circuit after 1 hour if my cable (133% level of insulation) is operating at <20A of SLG fault current.

Any help is appreciated!
 