Hello forum,
Can this be clarified per the scenarios as stated below?
A) If a #3 AWG THWN-2 wire is used to feed loads but terminated on 60C terminations then ampacity of that conductor is only 85A and not 115A. Similarly if its terminated on a 75C termination then its 100A.
B) Does the equipment provision as stated in 110.14(C)(1) is the circuit-breaker?
C) If the equipment is listed for 60C and 75C terminations and #1 AWG THWN is being used for a circuit rated 100A does that mean 250.122 (B) kicks in and needs to be addressed?
Wires not used for ampacity adjustment or correction factors. Thank you.
Can this be clarified per the scenarios as stated below?
A) If a #3 AWG THWN-2 wire is used to feed loads but terminated on 60C terminations then ampacity of that conductor is only 85A and not 115A. Similarly if its terminated on a 75C termination then its 100A.
B) Does the equipment provision as stated in 110.14(C)(1) is the circuit-breaker?
C) If the equipment is listed for 60C and 75C terminations and #1 AWG THWN is being used for a circuit rated 100A does that mean 250.122 (B) kicks in and needs to be addressed?
Wires not used for ampacity adjustment or correction factors. Thank you.