I have some 1 1/2 EMT with 42 #12 xhhw current carrying conductors. What is maximum over current device for these circuits
This in a dry or wet location?
This in a dry or wet location?
Is it going to make a difference with 42 ccc's?
I came up with 10 amps - dry / 5 amps wet.
To properly apply 310.15B16 one must first look at 310.104A.
In a dry location starting ampacity of #12 is 30 amps.
In a wet location starting ampacity of #12 is 25 amps.
I came up with 10 amps - dry / 5 amps wet.
I came up with 15 amps - dry or wet
How so?
I came up with 15 amps - dry or wet