Table 310.15(B)(3)

Status
Not open for further replies.

jbolen

Senior Member
I have a 2 inch conduit with 16 #12 XHHW current carrying conductors. What size breaker can I use for over current.
 
. . . assuming you are using 90C wire
Help me out here. I see that XHHW appears in both the 75C and 90C columns. I had not noticed that before, as I never specify that type insulation. So how does one determine whether the wire you buy is the 75C version or the 90C version? :?
 
Help me out here. I see that XHHW appears in both the 75C and 90C columns. I had not noticed that before, as I never specify that type insulation. So how does one determine whether the wire you buy is the 75C version or the 90C version? :?

Yeah that surprised me years ago that a wire in a wet location is rated less than in a dry location. If the insulation has a -2 after the letters then it is 90C for both wet and dry as Curt mentioned above.
 
OK. Thanks. And now that I have learned something new today, an event that should happen every day, I can go home. Right? :lol:
 
Yes the devil is in the details. If this were a test question you would really need to know if the location were wet or dry. Wet drops you below 15 amps after derating.
 
I have a 2 inch conduit with 16 #12 XHHW current carrying conductors. What size breaker can I use for over current.

I think the other posters have covered it pretty well, however, I would suggest that sometimes the answer comes in the form of another question that goes something like "why would anyone do that?".
 
Heck, if this were a test question you would need to know the sort of load being served. If this were a bunch of motor circuit conductors.....

-Jon
 