What is the history and substantiation for Table 310.15(B)(6)?
The current carrying capacity is significantly increased per this table for dwelling units only. If I have a 200A service and plan to use type TW conductors, the table permits me to use 2/0 where 310.16 would require at least 250-kcmil. If I load that service to close to 200A, wouldn't the temperature exceed 60 degrees C?
Can it be inferred that dwellings typically don't load services to their maximum rating where as a non-dwelling is more likely to? This seems to be a hazardous assumption.
The current carrying capacity is significantly increased per this table for dwelling units only. If I have a 200A service and plan to use type TW conductors, the table permits me to use 2/0 where 310.16 would require at least 250-kcmil. If I load that service to close to 200A, wouldn't the temperature exceed 60 degrees C?