I have a situation where the contractor needs to install parallel sets of cables in an underground conduit for the service.
System is 120-208, 3ph-4w
Occupancy is Multi-Family residential
I have to derate for more than 3 CCc per Table 310.15(C)(1)
Question is do you use 4-6 or 7-9 for number of conductors?
I believe the neutral would not count as a CCC but Table 310.15(C)(1) says Number of Conductors (not Number of CCC conductors).
Of course, to complicate things the asterisk below the table says:
*Number of conductors is the total number of conductors in the raceway or cable, including spare conductors. The count shall be adjusted in accordance with 310.15(E) and (F).