According to NEC art. 90.5 Mandatory Rules, Permissive Rules, and Explanatory Material. it is stated:
Permissive rules of this Code are those that identify actions that are allowed but not required, are normally used to describe options or alternative methods, and are characterized by the use of the terms SHALL BE PERMITTED or shall not be required.
310.60 Conductors Rated 2001 to 35,000 Volts.
(A) Ampacities of Conductors Rated 2001 to 35,000
Volts. Ampacities for solid dielectric-insulated conductors
shall be permitted to be determined by tables or under engineering supervision, as provided in 310.60(B) and (D).
Informational Note No. 1: For ampacities calculated in
accordance with 310.60(A), reference IEEE 835-1994 (IPCEA
Pub. No. P-46-426), Standard Power Cable Ampacity
Tables, and the references therein for availability of all factors and constants.
The reference IEEE 835_1994 describes the cable for which the ampacity is indicated. NEC does not.
However if your cable does not match any cable type from the list you may calculate the ampacity according to the methodology attached here based-generally-on Neher and McGrath theory. You also may change the number, the diameter, the distance between ducts and so on.