That is my guess.Do you mean T310.15(B)(2)(b)?
No. First simple fact effecting the outcome of the calculation is the adjustment factor of 1.00 is for 30 degrees in one table and 40 degrees in the other.Would I get the same answer from 310.15 b2b and if I corrected the ampacities in 310.15 b 16 with Table 310.15(B)(2)(a)?
No. First simple fact effecting the outcome of the calculation is the adjustment factor of 1.00 is for 30 degrees in one table and 40 degrees in the other.
What kind of conductor are you using? Most common applications are all conductors from 310.15 (B) (16), which that table is based on 60, 75 and 90 degree rated conductors used at an ambient temp of 30C. You will not use (B)(2)(b) for adjustments to conductors selected from (B)(16)if I had a room with a 45 degree Celsius ambient temperature...which correctional table do I use? 310.15B2a or 310.15B2b?
im confused appreciate your feedback