Based on the 2011 NEC how would you derate the following:
using 6 single conductor 4/0 cables (90 degree C) running through a conduit or raceway (industrial environment where only qualified persons will service the equipment so can run in raceway per 400.14). Per NEC 400.14 "Where more than three current carrying conductors are installed within the raceway, the allowable ampacity shall be reduced in accordance with Table 400.5(A)(3).
My confusion lies in the fact that Table 400.5(A)(3) is "Adjustment Factors for More Than Three Current-Carrying Conductors in a Flexible Cord or Cable". My cable is not multi conductor, however, but rather 6 separate single conductor tables.
Do I use the D1 column for the single conductor cable and then use the 80 percent derating factor in Table 400.5(A)(3) even though it seems this is the derating factor for a multi-conductor cable containing more than 3 current carrying conductors in it?
I understand the reason for the derating factor due to the increased heat generated by multiple current carrying in a multi conductor cable but I would think that single conductor cables might be derated at a different derating factor as they have more surface area to dissipate the heat generated in them.
Any help would greatly be appreciated.
John
using 6 single conductor 4/0 cables (90 degree C) running through a conduit or raceway (industrial environment where only qualified persons will service the equipment so can run in raceway per 400.14). Per NEC 400.14 "Where more than three current carrying conductors are installed within the raceway, the allowable ampacity shall be reduced in accordance with Table 400.5(A)(3).
My confusion lies in the fact that Table 400.5(A)(3) is "Adjustment Factors for More Than Three Current-Carrying Conductors in a Flexible Cord or Cable". My cable is not multi conductor, however, but rather 6 separate single conductor tables.
Do I use the D1 column for the single conductor cable and then use the 80 percent derating factor in Table 400.5(A)(3) even though it seems this is the derating factor for a multi-conductor cable containing more than 3 current carrying conductors in it?
I understand the reason for the derating factor due to the increased heat generated by multiple current carrying in a multi conductor cable but I would think that single conductor cables might be derated at a different derating factor as they have more surface area to dissipate the heat generated in them.
Any help would greatly be appreciated.
John