Hi. I work in the mining industry and I'm trying to figure out how to apply table 400.5(A)(2) of the code. We have a piece of equipment that is 1200' away from it's power source on the surface. we will probably run G-GC underground. Let's say the connectors that I'm using for my cable are rated at 500A, but only accept 350 KCM cable. Table 400.5(A)(2) says my 350 KCM G-GC is rated for 381A. So if I'm outside of the panel and just running my cable I'm okay. My problem is when I hit my distribution panel or the piece of equipment I'm powering. My connector limits me to 350 KCM. Section 110.14(C)(1) says that I have to use table 310.15(B)(16) unless my equipment is explicitly marked otherwise. So, when I leave my connector with my cable, and land it on my circuit breaker, I have to assume that the ampacity of the wire is on the order of 310 Amps. is there something I'm overlooking code-wise that makes using 400.5(A)(2) acceptable to use in a temporary situation? (temporary being 6 months to 2 years).
If you can't use 400.5(A)(2), why is it in the code at all?
If you can't use 400.5(A)(2), why is it in the code at all?