Table 430.248
Maryland
Buildin engineer 1
Can someone explain to me how does the table 430.248 1/4 HP makes 5.8 Amp. on 115V
please correct me because I strongly beleive that I'm wrong
1/4HP motor
746W/4=186.5W
186.5W/115V=1.62A
what am I missing to reach 5.8A. beacuse the table show that for a single phase is not 1.62A
Thanks
You're missing the motor efficiency: 1.62A / 5.8A = 28% implied efficiency.
In other words, a 100% efficient motor could convert 186.5W of electrical input to 1/4 HP of mechanical output, and at 115V it would use only 1.62A. The NEC wants you to design the circuit for a worst-case efficiency of 28%.
Cheers, Wayne
Also need power factor
Yes, definitely I should have included that. I guess one could call power factor "current to electrical power" efficiency. And the typical quantity you'd call motor efficiency would be "electrical power to mechanical power" efficiency. The calculated 28% would be the product of the two.