Ravenvalor
Senior Member
- Location
- Piedmont region of NC
Hello,
Does anyone know if one can install 16 - current carrying #12 conductors through about 20' - of 3/4" EMT and keep them on a 20-amp circuit breaker if each conductor is pulling 9-amps?
According to my interpretation of Table B.310.15(B)(2)(11) ** In the 2014 Code Book if I use only 9 - conductors then it is legal. What is it about the 2 - ** in the Table on the third row that would prevent me from using a 20-amp breaker under the conditions described above? The percent values are both 70%.
Thank you,
Does anyone know if one can install 16 - current carrying #12 conductors through about 20' - of 3/4" EMT and keep them on a 20-amp circuit breaker if each conductor is pulling 9-amps?
According to my interpretation of Table B.310.15(B)(2)(11) ** In the 2014 Code Book if I use only 9 - conductors then it is legal. What is it about the 2 - ** in the Table on the third row that would prevent me from using a 20-amp breaker under the conditions described above? The percent values are both 70%.
Thank you,