Table III of the 1957 Neher-McGrath paper
morgan3520
Dallas, TX
Electrical Engineer
Is anyone familiar with how to use Table III. Skin Effect in %/ in Solid Round Conductor and in Conventional Round Concentric, Strand Conductors, 100 F(x), Skin Effect % of the 1957 Neher-McGrath paper?
Get xs from equation 22 using the DC resistance per foot of the conductor and the ks factor provided in Table II. for concentric round conductor construction which is 1.0. Then in Table III. read the skin effect's contribution to the total resistance as a percentage of the DC resistance for that specific value of x.
For example, if xs was 2.14 then from Table III. the skin effect would contribute 10.05% of the DC resistance.
Consider this result in Fig. 1, where for F(x) = 0.1 (i.e., a 10% skin effect), one can read off Rdc /k ≈ 10. And then from equation 22, xs = 6.80 / √(Rdc/ks) = 6.80 / √(10/1.0) = 2.15 which is consistent with the value of xs that was picked above.
Thank you.