Tables 312.6 (A), 312.6 (B)?

Status
Not open for further replies.

The Iceman

Senior Member
Location
Florida
I'm currently studying the Stallcup's Master Electrician's Study Guide. Most of this book has been a review, but I'm stuck on tables 312.6 (A), and 312.6 (B). Can anyone elaborate on these tables. Being a journeyman I'm embarrassed to admit it, but I'm not sure the difference between them.
 
If you do not mind writing in your code book, here is some advice.


Table 312.6(A)
On the top of the page just above the title of the table write this:

" Conductors not leaving or entering opposite wall - Gutter Space"


Table 312.6(B)
On the top of the page just above the title of the table write this:
"conductors leaving or entering opposite wall - Straight in"


does this help? If not let me know, and I will elaborate further.
 

The Iceman

Senior Member
Location
Florida
Thanks Pierre thats a good idea. I guess thats were I'm getting stuck. Conductors not entering or leaving opposite wall 312.6 (A), and Conductors entering or leaving opposite wall 312.6 (B)?
 
The Iceman said:
Thanks Pierre thats a good idea. I guess thats were I'm getting stuck. Conductors not entering or leaving opposite wall 312.6 (A), and Conductors entering or leaving opposite wall 312.6 (B)?





Let me see if I can find an illustration to show you what I mean. if not an illustration, I have pictures...:grin:
 

The Iceman

Senior Member
Location
Florida
Pierre C Belarge said:
Let me see if I can find an illustration to show you what I mean. if not an illustration, I have pictures...:grin:

Thanks, I would appreciate it. I have read 312.6 (B) (1) and (2) over and over. I'm just not getting it.
 
Iceman
Here are a few pictures that I hope will help you to understand Tables 312.6(A)&(B) a little more.



These pictures show Table 312.6(A). As you can see the supply conductors to the panel enter a wall of the panel that is not OPPOSITE of the lugs they have been terminated to.
condAmpacity1.jpg



Panels11.jpg



This picture shows Table 312.6(B). As you can see the supply conductors enter the panel directly opposite from the lugs they have been terminated to.
PanelBoard.jpg


The last picture shows both tables. As you can see one set is entering the enclosure and one set is leaving the enclosure. The set on the top side of the actual disconnect is Table 312.6(B), and the set on the left side of the disconnect is Table 312.6(A).
Disco_NeutralIsolate1.jpg
 

JohnJ0906

Senior Member
Location
Baltimore, MD
Pierre C Belarge said:
John
I meant no disrespect to you.
"A picture is worth a thousand words"...so my post is like 4000 words. :wink:

I just can't type that much....

Actually, it helped ME understand more clearly. :smile:
 