augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Apr 7, 2017 #1 Does the Code address the method of sizing conductors on motors larger than those listed in Table 430.250 ?
Does the Code address the method of sizing conductors on motors larger than those listed in Table 430.250 ?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Apr 7, 2017 #2 I would assume motors of that size may be over 1000 V but I am not certain. If so then part XI of 430 would apply. I guess one would use the nameplate????
I would assume motors of that size may be over 1000 V but I am not certain. If so then part XI of 430 would apply. I guess one would use the nameplate????
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Apr 7, 2017 #3 600HP 480v Nameplate 655 amps Asked about sizing conductors. Electrician states its ACL start.. I have my doubts
600HP 480v Nameplate 655 amps Asked about sizing conductors. Electrician states its ACL start.. I have my doubts