Hello all,
I'm currently working on creating a SCADA system for fire alarm in a company. I'm taking the input for SCADA's PLC by utilizing the existing Fire Alarm Control Panel (FACP) that has 10 zone detection which i need all this 10 zone input for my 24 VDC relay.
The problem is when I try to tap the input from the FACP terminal, it detects fault in the control panel and the voltage drop to 12 VCD. After some research i found out that this happen because I disrupt the Resistance in the zone's circuit as i connect my relay (with 700 Ohm coil resistance) in parallel with the zone circuit.
The circuit is Class B wiring, with 10k Ohm end of line resistance, 50 Ohm maximum Loop Resistance, and it says 1,35 mA maximum per zone circuit (excluding the end of line resistance current).
Any idea guys? I'm trying to isolate my work area only in the FACP. Maybe using any electronic device (transistor or etc) to take the input signal.
I also attach some ilustration on the class B wiring circuit
Sincerely thanks,
I'm currently working on creating a SCADA system for fire alarm in a company. I'm taking the input for SCADA's PLC by utilizing the existing Fire Alarm Control Panel (FACP) that has 10 zone detection which i need all this 10 zone input for my 24 VDC relay.
The problem is when I try to tap the input from the FACP terminal, it detects fault in the control panel and the voltage drop to 12 VCD. After some research i found out that this happen because I disrupt the Resistance in the zone's circuit as i connect my relay (with 700 Ohm coil resistance) in parallel with the zone circuit.
The circuit is Class B wiring, with 10k Ohm end of line resistance, 50 Ohm maximum Loop Resistance, and it says 1,35 mA maximum per zone circuit (excluding the end of line resistance current).
Any idea guys? I'm trying to isolate my work area only in the FACP. Maybe using any electronic device (transistor or etc) to take the input signal.
I also attach some ilustration on the class B wiring circuit
Sincerely thanks,