Are tamper proof receptacles required in commercial work?
G gbuschling Member Location Chesapeake Beach, Md Nov 29, 2010 #1 Are tamper proof receptacles required in commercial work?
chris kennedy Senior Member Location Miami Fla. Occupation 60 yr old tool twisting electrician Nov 29, 2010 #3 No, see 406.11 in your 08.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Nov 29, 2010 #4 Just for the record the NEC defines them as tamper resistant not tamper proof.
ceb58 Senior Member Location Raeford, NC Nov 29, 2010 #5 Only if the plumbers keep sticking keys and paper clips in the recpt.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Nov 29, 2010 #6 Tamper resistant recep. are required in some patient care areas esp. pediatric areas.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Nov 30, 2010 #7 And will be required in elementary schools under the 2011 code.
raider1 Senior Member Staff member Location Logan, Utah Nov 30, 2010 #8 don_resqcapt19 said: And will be required in elementary schools under the 2011 code. Click to expand... Interesting take Don, so you are saying that an elementary school would be a child care facility in accordance with 406.14? I will have to do a little more thinking on this one. Chris