Tamper resistant outlets

Status
Not open for further replies.
Ihave
I have not read up on the '17 code but the '14 code requires GFCI WR, TR with Extra Duty in-use cover.

Is the 5' overhang exception still in play to not have bubble covers? or do all outside receptacles require those now regardless of where they are located? VA is not on the 14 NEC so I dont have it
 
Do the gfi outlets outside my house need to be tamper resistant?


Sent from my iPhone using Tapatalk

It depends on the code edition in your area at time of installation.

I'm talking about current nec code


Sent from my iPhone using Tapatalk

And if you are on the 2014......

406.12 (A) from the 2014 says in all the areas specified by 210.52, so yes they do.

and........

.... the '14 code requires GFCI WR, TR with Extra Duty in-use cover.

...pretty much sums it up.:happyyes:

Technically yes, practically no.

Unfortunately with tr the practicality and common sense ship has sailed with manufacturers and lobbyists at the helm.:thumbsdown:
 
Is the 5' overhang exception still in play to not have bubble covers? or do all outside receptacles require those now regardless of where they are located? VA is not on the 14 NEC so I dont have it
406.9 says receptacles in areas protected from weather or damp locations are exempt from space helmet covers. That often translates to down on the front porches and up in the eves.
 
And if you are on the 2014......



and........



...pretty much sums it up.:happyyes:



Unfortunately with tr the practicality and common sense ship has sailed with manufacturers and lobbyists at the helm.:thumbsdown:

We are not really still whining about TR receptacles are we?:D

Once I saw the numbers used for the substantiation for TR I changed my view and support the requirement.
 
We are not really still whining about TR receptacles are we?:D

No- just about the extreme to which it has been applied and I believe that if someone doesn't want them in their own home, they should not be required to have them......So yeah, whining:lol:

I do believe they should absolutely be required per 517.18 and 406.12 for pediatric areas, daycare/childcare facilities etc.



But whats done is done- the requirement is here, has been for a while, and isn't going anywhere so install we shall.:)
 
No- just about the extreme to which it has been applied and I believe that if someone doesn't want them in their own home, they should not be required to have them......So yeah, whining:lol:

:D

So no need to require cover on boxes either? :p


The numbers were huge, if I recall something like 7,000+ emergency room visits a year due to shocks from outlets.

Now I am always suspect of numbers and studies, always wondering who funded them and what the goal was but if I was on a CMP of an electrical safety code it would be tough to justify not doing something.

I really don't see this code change as a money generator for the manufacturers. Now if the code change required electronics and motorized shutters then they could make some money. :p
 
:D

So no need to require cover on boxes either? :p


The numbers were huge, if I recall something like 7,000+ emergency room visits a year due to shocks from outlets.

Now I am always suspect of numbers and studies, always wondering who funded them and what the goal was but if I was on a CMP of an electrical safety code it would be tough to justify not doing something.

I really don't see this code change as a money generator for the manufacturers. Now if the code change required electronics and motorized shutters then they could make some money. :p

I am not against safety. Selfishly, I don't like TR's because they are a PITA to insert test probes into.

But, out of curiosity, do you know how much the 7,000+ ER visits have dropped since TR receptacles have been required?
 
I am not against safety. Selfishly, I don't like TR's because they are a PITA to insert test probes into.

But, out of curiosity, do you know how much the 7,000+ ER visits have dropped since TR receptacles have been required?

I'd rather know the ratio of visits attributable to non TR's vs. TR's.
 
What "5' overhang exception" are you referring to?

VA does not have such an exception/amendment to the IRC in its USBC/VCC.

Electrical amendments to the IRC start at page 70.

http://www.dhcd.virginia.gov/images/SBC/CodeBooks/2012 Virginia Construction Code.pdf

that receptacles mounted outdoors but with at least 5' of overhang didnt need bubble covers (like on a porch), but those mounted directly to the side of the house or with less than 5' protection did need bubble covers.
 