Where are tamper resistant receptacles required per code. Specifically NYC. Looking for location or spec section, appreciate the help
406.11 Tamper-Resistant Receptacles in Dwelling Units. In all areas specified in 210.52, all 125-volt, 15-and 20-ampere receptacles shall be listed tamper-resistant receptacles.
Why 2008?You'll need to look at the requirements in the 2008 NEC. This from the 2008:
NYC is under the 2008 NEC with it's own amendments. Is this question about a dwelling unit?Why 2008?
No, a commercial space.NYC is under the 2008 NEC with it's own amendments. Is this question about a dwelling unit?
Then don't worry about the TR receptacles.No, a commercial space.