Tamper resistant receptacles 406.12

reyamkram

Senior Member
Location
Hanover park, il
Per 406.12 States receptacles in the areas specified in 406.12 1 through 8 shell B listed tamper resistant so does that mean if I install tamper resistant receptacles they must be listed or when I I replace old receptacles I need to install tamper resistant receptacles per 20/20 NEC is installing tamper-resistant receptacles mandatory to replace when I removed old receptacles thank you for any and all information
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Not likely you van get a non TR receptacle in 15-20 a 125 V. A replacement receptacle must meet current requirements for location, so may need to be TR, AFCI, GFCI, WR,
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Not likely you van get a non TR receptacle in 15-20 a 125 V. A replacement receptacle must meet current requirements for location, so may need to be TR, AFCI, GFCI, WR,
Lots of 15 and 20 amp duplex non-TR receptacles on the shelves at the local big box stores.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
When I was working I had to special order nonTR recptacles at the supply house as they catered to resi companies
 

shortcircuit2

Senior Member
Location
South of Bawstin
Per 406.12 States receptacles in the areas specified in 406.12 1 through 8 shell B listed tamper resistant so does that mean if I install tamper resistant receptacles they must be listed or when I I replace old receptacles I need to install tamper resistant receptacles per 20/20 NEC is installing tamper-resistant receptacles mandatory to replace when I removed old receptacles thank you for any and all information
406.4(D)(5) requires replacement to be TR where required. Don't forget AFCI per 406.4(D)(4)
 