hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have plans with two floors. First floor is divided into two: one space has retail space and second is a dwelling unit. The second floor is divided into two and has two dwelling units.
The kitchen of each dwelling unit has the following:
1. One dedicated duplex receptacle for microwave, stove
2. One dedicated duplex receptacle for just says appliance #1
3. One dedicated duplex receptacle for just says appliance #2
4. One dedicated duplex receptacle for refrigerator
5. One dedicated duplex receptacle for dishwasher
I researched and looked at NEC 2014 section 406.12 Tamper-Resistant exception #3:
“Exception to (A), (B), and (C): Receptacles in the following locations shall not be required to be tamper resistant:
(3) A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and plug-connected in accordance with 400.7(A)(6), (A)(7), or (A)(8).”
Am I correct that tamper resistant receptacles are not required kitchen four items listed above based on exception #3 or am I incorrect and I do need tamper resistant receptacles items listed above and exception #3 does not apply?
The kitchen of each dwelling unit has the following:
1. One dedicated duplex receptacle for microwave, stove
2. One dedicated duplex receptacle for just says appliance #1
3. One dedicated duplex receptacle for just says appliance #2
4. One dedicated duplex receptacle for refrigerator
5. One dedicated duplex receptacle for dishwasher
I researched and looked at NEC 2014 section 406.12 Tamper-Resistant exception #3:
“Exception to (A), (B), and (C): Receptacles in the following locations shall not be required to be tamper resistant:
(3) A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and plug-connected in accordance with 400.7(A)(6), (A)(7), or (A)(8).”
Am I correct that tamper resistant receptacles are not required kitchen four items listed above based on exception #3 or am I incorrect and I do need tamper resistant receptacles items listed above and exception #3 does not apply?