Tamper resistant

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have restaurant more than 100 occupants assembly and in dinning area receptacles are provided height 18 inch above floor.

I am looking at NEC 2017 section 406.12(6) says subset of assembly occupancies in 518.2 to include places if waiting transportation, gym, skating rinks and auditoriums.

Its not clear when that section mentions to include does it mean that only these assembly that are included i.e transportation, gym, skating rinks and auditoriums to be tamper resistant or does it mean 518.2 subset of assembly which then also include restaurant as well?
 