Tamper resistant

Status
Not open for further replies.

JJWalecka

Senior Member
Location
New England
The use of tamper resistant receptacles is required by section 406.11 in the 2008 NEC. That article refers to 210.52.
?In areas specified in 210.52, all 120 volt, 15- and 20-ampere receptacles shall be tamper resistant?

Question: Is the small appliance GFCI considered part of the dwelling unit tamper resistant requirement. What about Bathrooms?

Unless I read it wrong the receptacles required to be tamper proof shall be all but
Those that are part of a luminaries, Controlled by a switch located in cabinets or cupboards, or located more than 5.5 feet above finish floor

Perhaps I am over analyzing this

Thanks JJ
 
I believe that there are receptacles, such as the garage door motor recep. , that do no need a Tamper resistant recep. However, it is easier to just install all the recep. as TR type then to pick and choose.

I could argue the fact that art. 210.52 states that it includes all recep. in addition to the 4 listed. To me this actually would mean that even those 4 situation should be TR since they are mentioned in art. 210.52

Yes, bath and Kitchen counter need TR recep.
 