NEMA Proposal 18-40 Section 406.11(New)
Panel Action: Accept Vote: 10-1-1
Commentary: NEMA proposal 18-40 would require the use of tamper resistant receptacles throughout dwellings. The overwhelming consensus was to accept this proposal, but a considerable amount of time was spent debating whether the requirement for tamper resistant receptacles should be limited to only those that are easily accessible to children. For instance, it was questioned whether the receptacles behind refrigerators, or on walls behind counter tops, should need to comply. Panel members also questioned the ease with which attachment plugs could be inserted into tamper resistant receptacles, resulting in the writing of the following panel statement:
?The panel is concerned about the possible increased insertion force required for our aging population. The panel requests data concerning the amount of force necessary to insert a plug into the shutter and the amount of force necessary to fully insert a plug into a tamper-resistant receptacle?.
The panel finally agreed to accept the proposal without any location restrictions to see what comments were generated during the public review phase. The IAEI representative voted against the proposal. The IEC representative abstained from the voting.