- Location
- New Jersey
- Occupation
- Journeyman Electrician
We recently installed some Heavy Duty 200 amp Eaton non-fused disconnect switches {model DH364UGKN3NP}, the circuit voltage is 480 volts. They contain Tangential KO's which were used with 1.5" EMT leaving a few of the larger KO's intact (KO goes up to 2.5"). The question arose whether or not these Tangential KO's would need a bonding bushing to comply with 250.97. It seems that the KO type, Tangential is not listed in 250.97 and the KO's are specifically listed by the manufacturer as being Tangential. The other question arose as to how to find out if a particular KO is suitable for bonding over 250 volts as outlined in the exception in 250.97.
One other thing, each conduit contains a copper EGC properly terminated on both ends and the circuit originates in a distribution board with field punched 1.5" KO's. Would this make the entire first paragraph of this post moot?
http://www.eaton.com/Eaton/Products...itches/HeavyDuty/Non-Fusible/index.htm#tabs-2
One other thing, each conduit contains a copper EGC properly terminated on both ends and the circuit originates in a distribution board with field punched 1.5" KO's. Would this make the entire first paragraph of this post moot?
http://www.eaton.com/Eaton/Products...itches/HeavyDuty/Non-Fusible/index.htm#tabs-2