Looking to add a tankless water heater to our facility (we have no hot water presently). In looking online at what's available, Rheem wants to sell us a 36kW heater to get 4gpm. Maybe they think we're melting ice, but we're in south Florida. I can't imagine potable water ever coming out of the pipe lower than 55F and that would be that 1-2 days per year when we get that arctic clipper and it gets down into the 40's at night. Other manufacturer's say their 1.1kW heater will do 3GPM, so we know we can't rely on manufacturer's data, from any of the manufacturers.
Two questions:
Question 1:
So here's what I came up to determine what we need assuming 100% efficiency if we want 4GPM:
So I'm thinking in the range of 4kW will be fine to get 4GPM.
Question 2:
Now to the voltage.
These heaters come in 120V & 240V single phase and also in 208V 3p.
Does everyone agree I can run a 240V heater at 208V 1p (2 legs of my 208Y) and I just need to size my breakers & conductors using the 208 in my calcs to determine the amperage?
I'm not saying that's what we'll do; I just want to affirm that that option is on the table.
Thanks!
Two questions:
Question 1:
So here's what I came up to determine what we need assuming 100% efficiency if we want 4GPM:
So I'm thinking in the range of 4kW will be fine to get 4GPM.
Question 2:
Now to the voltage.
These heaters come in 120V & 240V single phase and also in 208V 3p.
Does everyone agree I can run a 240V heater at 208V 1p (2 legs of my 208Y) and I just need to size my breakers & conductors using the 208 in my calcs to determine the amperage?
I'm not saying that's what we'll do; I just want to affirm that that option is on the table.
Thanks!