When applying tankless water heaters to electrical load calculations. Do you apply the demand factor or is it figured at 100%
Optional method. Total renovation Installing new 200amp service, but trying to keep it from going to 400amp with 112 amp water heater. My demand is now 119amps without water heaterAre you doing a standard or optional calc?
new house or addition to existing?
What demand factor? if you have 4 or more appliances then yes you can use 75% but if not the water heater is calculated at 100% as it is tankless so it is not continuousWhen applying tankless water heaters to electrical load calculations. Do you apply the demand factor or is it figured at 100%
if you don't want to go over 200 A service, get a gas water heater.Optional method. Total renovation Installing new 200amp service, but trying to keep it from going to 400amp with 112 amp water heater. My demand is now 119amps without water heater
I get that the code is the code, but how is a tankless water heater not continuous, or potentially so? Someone leaves the tap open for 4 hours, it would run continuously. I found a table for electric water heater recovery times, and with 4500 watts of heating, assuming the water coming in is at 40F and you're heating it to 120F, the recovery is 23 gal/hr if all the water in the tank starts at 40F. As long as the tank is under 69 gallons, the storage water tank is not a continuous load in practice, unlike what the code says.What demand factor? if you have 4 or more appliances then yes you can use 75% but if not the water heater is calculated at 100% as it is tankless so it is not continuous
4500 Watts is 15,354 btu/hour.I get that the code is the code, but how is a tankless water heater not continuous, or potentially so? Someone leaves the tap open for 4 hours, it would run continuously. I found a table for electric water heater recovery times, and with 4500 watts of heating, assuming the water coming in is at 40F and you're heating it to 120F, the recovery is 23 gal/hr if all the water in the tank starts at 40F. As long as the tank is under 69 gallons, the storage water tank is not a continuous load in practice, unlike what the code says.
I just went thru this last year with a huge tankless on new smaller house, it took four 2-pole 40's if I remember.I get that the code is the code, but how is a tankless water heater not continuous, or potentially so?
Yes, I am not sure what demand the op is talking about so I just thru out one that perhaps he was talking about.Isn't that 75% factor with the standard calculation only? All Non-HVAC loads in the optional calculation get a 40% factor once you're past the 10KW threshold.