ron
Senior Member
- Location
- New York, 40.7514,-73.9925
800A feeder with paralleled 500's.
We will be tapping the 800A feeder for a 100A circuit to serve a VDF/motor.
Do you tap one set of the main feeder run, or do you need to tap both main feeders with 1/0's then tie them together at a 100A temrination in the VFD (which would be difficult to get sufficient lugs in the VFD).
Just overthinking ....
We will be tapping the 800A feeder for a 100A circuit to serve a VDF/motor.
Do you tap one set of the main feeder run, or do you need to tap both main feeders with 1/0's then tie them together at a 100A temrination in the VFD (which would be difficult to get sufficient lugs in the VFD).
Just overthinking ....