H Hendrix Senior Member Location New England Feb 25, 2013 #1 I have seen this numerouse times in older buildings. Don't think you can do it anymore. Can someone quote the code section please?
I have seen this numerouse times in older buildings. Don't think you can do it anymore. Can someone quote the code section please?
david luchini Moderator Staff member Location Connecticut Occupation Engineer Feb 25, 2013 #2 See 240.21. Conductors supplied under the provisions of 240.21(A) through (H) shall not supply another conductor except through an overcurrent protective device meeting the requirements of 240.4. Click to expand...
See 240.21. Conductors supplied under the provisions of 240.21(A) through (H) shall not supply another conductor except through an overcurrent protective device meeting the requirements of 240.4. Click to expand...
iwire Moderator Staff member Location Massachusetts Feb 25, 2013 #3 Keep in mind that the section David posted applies only to feeders and not service conductors.