dwinchel
Member
- Location
- Forth Worth, TX
At an existing indoor 750kVA 4160/480v unit substation that has two breaker feeders in the switchgear section. The transformer primary OCPD fuse is 100E. There is no space available to add another feeder breaker. The design calls for connecting 2x3(700mcm) cables at the switchgear bus and run that over to 1000 amp Frame/900 amp trip wall mounted breaker disconnect OCPD. The total run is less than 25 feet at an adjacent wall. Can I please get a double check that I met requirements of 240.21(B)(2) taps not over 25 feet long. Is thee any other considerations? thanks