Originally posted by hienlam:
can i make two splices at secondary side of transformers.???. one feed the chiller and one feed site lighting..???..does nec allow me to do this...(nec mention about the tap rule, but did not say how many...)
please advise...
HELP...
From the ROP
"
Substantiation:
As 240.21(C)(3)(1) is now written, it is unclear whether or not it is referring to a single set of secondary conductors or multiple sets of secondary conductors going to different overcurrent devices. For example, a transformer secondary feeding two unequally-rated overcurrent devices. I believe the NEC intent is to have these two sets of conductors be the same size, however, the existing wording can lead someone to install two sets of differently sized conductors whose combined ampacity is more than the secondary current rating of the transformer.
Panel Meeting Action: Accept in Principle
Revise existing 240.21(C) to read as follows: "Each set of conductors feeding separate loads shall be permitted to be connected to a transformer secondary, without overcurrent protection at the secondary, as specified in 240.21(C)(1) through (6)."
Panel Statement:
By revising the text in the main body of 240.21(C), the panel has met the intent of the Submitter and is also clarifying the requirement for multiple loads in general."
In other words, yes is the panel's intent as reflected in the change above that will be in the 2005 edition of the NEC, assuming this goes through in the comment stage (the panel vote was 12 - 0).