Re: tap at secondary
240.21(C)(3)(1) is listed as Industrial installations only. The poster did not say this was industrial. If not, I think 240.21(C)(2)(1a & b) might be interepted to allow this installation.
1a would assume the ampacity of the conductor to each panel would be adequate for the load.
1.b the conductors to each breaker would have ampacity equal to rating of each breaker. I would add that the sum of the breaker ratings would not exceed the rating of the transformer. You would also apply the logic that the panels should be grouped together.