I have a gentleman that wants to run power to a pole building for camper / trailer storage. He wants a 100 amp panel with power provided from and existing barn 160' from the pole building. At the barn he has a 200 amp meter and panel. He wanted me to run the new service from a 100 amp breaker inside the barn panel to the pole building 100amp panel. According to my calculations I will need 2/0 aluminum because of voltage drop to accomplish this. 2/0 will not fit the lugs of a 100 amp breaker and/or the lugs on a 100 amp main in the pole building panel. Here's the question: Can I tap the SE on the load side of the meter of the barn service if I put a 100 amp disconnect to feed the pole building panel? I will also have to increase the size of the new panel to use 2/0? I suggested the power company run a new service, but he's not fond of that. Any suggestions would be appreciated. Thanks.