Ok so I have 4000A service disconnect which feeds to 400A fused disconnect with 3 phase 2 sets of (4#3/0 AWG + 1 #3G) 10 feet or less from service disco.
These are feeder taps conductors so I asked to provide 250.122(G) equipment grounding conductor size. I am surprised at the response I got they provided 2 sets(4#3/0 + 350kcmilG). They say it comply per NEC 2014 section 250.122(G) equipment grounding conductor is not required to be larger than phase conductor. According to them 3/0=168 kcmil and 2x3/0 = 336 kcmil so it is not larger than phase. Yes they are providing 350kcmil each conduit.
Ok please correct me if I am wrong but should this not be 2 sets(4#3/0 + 3/0G)? Is feeder taps equipment grounding conductor size 3/0G or 350 kcmil?
These are feeder taps conductors so I asked to provide 250.122(G) equipment grounding conductor size. I am surprised at the response I got they provided 2 sets(4#3/0 + 350kcmilG). They say it comply per NEC 2014 section 250.122(G) equipment grounding conductor is not required to be larger than phase conductor. According to them 3/0=168 kcmil and 2x3/0 = 336 kcmil so it is not larger than phase. Yes they are providing 350kcmil each conduit.