MiloHEES
Member
- Location
- Angleton, TX
When applying the short-circuit formulas for conductors NEC (2014) Chapter 9, Table 8, should T1 be the temperature rating of the conductor (75C or 90C) or the ambient temperature?
I don't recall a short circuit calculation in the Chapter 9 Tables.
The published short circuit current tables that I have seen started with the rating of the conductor and not the ambient. The reasoning is that the conductor may be operating at close to its rating at the time of the short circuit.
The published short circuit current tables that I have seen started with the rating of the conductor and not the ambient. The reasoning is that the conductor may be operating at close to its rating at the time of the short circuit.