Voltage:
I have a 1600 amp breaker supplying a group of cabinets that each feed electric heating elements. The 1600 amp breaker feeds 9 conductors (3 per phase). Each of the existing heating element cabinets has a 500 amp breaker. The 500 amp breakers are fed by tap conductors that go to the main feed conductors. I would like to install two new cabinets, but they each only have a 250 amp main breaker. I would like to tap off the same main supply conductors as the other cabinets. The problem I run in to is the tap conductor sizing. Since the cabinet is 20 ft away from the main supply conductors (greater than 10 ft), I have to upsize it. The problem is that the appropriately sized conductors won't fit into the lugs of the 250 amp breakers. Can anyone think of a way around this? I would like to size the tap conductors for being 10 ft long, but in actuality they will be 20 ft. The main supply conductors are in an open-air tray up high. The tap conductors drop down out of the tray with their own conduits into the cabinets. This is an industrial setting. Below is a rough diagram:
Main supply conductors
======================== (A Phase - 3 conductors per phase)
========================(B Phase - 3 conductors per phase)
========================(C Phase - 3 conductors per phase)
|||............|||..............|||
|||............|||..............|||
|||............|||..............|||
500A Bkr 500A Bkr 250A Bkr
Cabinet Cabinet Cabinet (would like to install)
I have a 1600 amp breaker supplying a group of cabinets that each feed electric heating elements. The 1600 amp breaker feeds 9 conductors (3 per phase). Each of the existing heating element cabinets has a 500 amp breaker. The 500 amp breakers are fed by tap conductors that go to the main feed conductors. I would like to install two new cabinets, but they each only have a 250 amp main breaker. I would like to tap off the same main supply conductors as the other cabinets. The problem I run in to is the tap conductor sizing. Since the cabinet is 20 ft away from the main supply conductors (greater than 10 ft), I have to upsize it. The problem is that the appropriately sized conductors won't fit into the lugs of the 250 amp breakers. Can anyone think of a way around this? I would like to size the tap conductors for being 10 ft long, but in actuality they will be 20 ft. The main supply conductors are in an open-air tray up high. The tap conductors drop down out of the tray with their own conduits into the cabinets. This is an industrial setting. Below is a rough diagram:
Main supply conductors
======================== (A Phase - 3 conductors per phase)
========================(B Phase - 3 conductors per phase)
========================(C Phase - 3 conductors per phase)
|||............|||..............|||
|||............|||..............|||
|||............|||..............|||
500A Bkr 500A Bkr 250A Bkr
Cabinet Cabinet Cabinet (would like to install)