JimmysLimeade
EE Student & PV Design
- Utah
- PV Design
Tap conductor is #1.I am trying to figure out what part of a PV interconnection this applies to. I can't find a super clear definition of what is considered a tap conductor. Take this diagram for example:
Is the tap conductor at point 1, 2, or 3?
Should have clarified, this is just for ease of understanding on my endYour system would not be compliant, though. The most PV current that you can push through the tap is 32A
2 and 3 are the feeder
This is super helpful, thank you!Let's say your wire segments (1), (2), and (3) have ampacities of 100A, 200A, and 200A respectively. Then:
Wire segment (2) can receive 80A from the PV from one end, and 200A from the utility from the other end. In both cases, with an ampacity of 200A, it is protected at its point of supply at no more than its ampacity. It is not a tap conductor.
Wire segment (1) can also receive 80A from the PV from one end, and 200A from the utility from the other end. As its ampacity is only 100A, then it is a tap conductor with respect to the utility source. So it needs to comply with 2023 NEC 705.12(A)(3).
Wire segment (3) can receive 80A from the PV and 200A from the utility, all at one end. So it is a tap conductor, although we don't need to look at 240.21(B) for it, as it is covered by 705.12(A)(2).
He still has a problem with 705.12(B) in the main panel.Let's say your wire segments (1), (2), and (3) have ampacities of 100A, 200A, and 200A respectively. Then:
Cheers, Wayne
OK, but even just for understanding you should probably work with compliant drawings.Should have clarified, this is just for ease of understanding on my endnot meant to actually use
Assuming it has an ampacity of less than 200A, yes.Tap conductor is #1.
Most likely, although it would be OK if the main panel busbars have only two connections, the 200A main breaker and the feed-thru lugs. Meaning all other circuits have been relocated to the subpanel.He still has a problem with 705.12(B) in the main panel.
Although that definition is rooted in the paradigm that conductors have only one point of supply. Implicit in my answer is that the way to adapt that definition to multiple sources of supply is (a) add the OCPD ratings together when multiple sources of supply are combined at one end of the conductor and (b) treat the two ends separately when there is at least one source of supply at each end.The definition of a tap conductor is in 240.2. It's "a conductor, other than a service conductor, that has overcurrent protection ahead of its point of supply that exceeds the value permitted for similar conductors that are protected as described in 240.4."
I've certainly had the thought that 705 should just say something along the lines of what you say here, but it doesn't quite do that. So with respect to whether there is a clear definition of a tap conductor in the NEC, I think there is a clear definition in 240 when there's one source of supply, and not such a clear definition in cases covered by 705.Although that definition is rooted in the paradigm that conductors have only one point of supply. Implicit in my answer is that the way to adapt that definition to multiple sources of supply is (a) add the OCPD ratings together when multiple sources of supply are combined at one end of the conductor and (b) treat the two ends separately when there is at least one source of supply at each end.
Cheers, Wayne