dnj12345

Member
Hi I have a customer that has 40 amp 220v circuit to a oven they want to add another small oven next to the existing oven. I was going to junction the circuit and install tap conductors. But I dont want to overload the circuit. Anybody have any tips? Thanks In advance.
 
Hi I have a customer that has 40 amp 220v circuit to a oven they want to add another small oven next to the existing oven. I was going to junction the circuit and install tap conductors. But I dont want to overload the circuit. Anybody have any tips? Thanks In advance.

Can you tap a 40 amp range circuit?

210.19(3)
Exception No. 1: Conductors tapped from a 50-ampere
branch circuit supplying electric ranges, wall-mounted
electric ovens, and counter-mounted electric cooking units
shall have an ampacity of not less than 20 amperes and
shall be suffıcient for the load to be served.
 
Hi I have a customer that has 40 amp 220v circuit to a oven they want to add another small oven next to the existing oven. I was going to junction the circuit and install tap conductors. But I dont want to overload the circuit. Anybody have any tips? Thanks In advance.

If the first oven needs 40 amps then I doubt you can use it for the second oven. Read the notes to T220.55
 