Seem people are getting really creative these days with the shortages and long lead times on large equipment.
I have a buildout on a building that has nothing more than a 4000amp terminal box which is also located inside the building. This obviously creates some challenges since the 10 and 25ft tap rules would apply now. The service conductors are rated for up to 4000amps at 480 volt. They don't plan on having any more than 6 services but several other issues come to mind (emergency disconnect rule and GFI protection for 480v services).
Does 240.21 (c)(5) apply? (secondary conductors from a feeder tap transformer) I wouldn't think so since the transformer is a utility xfrmr and primary over current protection is not coordinated with our electrical installation.
240.21 (b)(2) says a 25' conductor can be used if the tap conductor is at least 1/3rd the rating of the over current device feeder the tap conductors. There is no over current device so now what?
I cant see how any of this even meets NEC requirements.
If the tap can were outside, it would be a different story...
Lately, we have been just installing the conduits to the utility transformer and pulling in the service conductor as required for each service. With the new emergency disconnect rule, I think we also need a switch ahead of the meter.
I have a buildout on a building that has nothing more than a 4000amp terminal box which is also located inside the building. This obviously creates some challenges since the 10 and 25ft tap rules would apply now. The service conductors are rated for up to 4000amps at 480 volt. They don't plan on having any more than 6 services but several other issues come to mind (emergency disconnect rule and GFI protection for 480v services).
Does 240.21 (c)(5) apply? (secondary conductors from a feeder tap transformer) I wouldn't think so since the transformer is a utility xfrmr and primary over current protection is not coordinated with our electrical installation.
240.21 (b)(2) says a 25' conductor can be used if the tap conductor is at least 1/3rd the rating of the over current device feeder the tap conductors. There is no over current device so now what?
I cant see how any of this even meets NEC requirements.
If the tap can were outside, it would be a different story...
Lately, we have been just installing the conduits to the utility transformer and pulling in the service conductor as required for each service. With the new emergency disconnect rule, I think we also need a switch ahead of the meter.