I have a 1000 ft perimeter outdoor lighting run. Voltage drop and temperature derating has the homerun at #6 awg. Can I tap off the main run with smaller wire to connect to the individual fixtures. I see in Article 410-67(C) where you can have tap conductors no greater than 6 feet in length. In Article 210-19(4) exception 1 which tells me the minimum wire size on a 40 amp or larger circuit must be 20 amp.
So if my home run is #6, The breaker for this circuit is 40 amps, then I could tap off the homerun with #12 wire to feed each fixture as long as it is not over 6 feet in length?
Thanks for the quick replies. This 1000 ft run is to the further most lights. I will have 10 175 watt 380 volt Metal Halide wall packs on the run. Site voltage is 220/380 volt 50 hz and the breaker will be a 2 pole 40. Don't really need this large a breaker but the shorter runs have more lights on the circuit so I was just keeping the breaker size the same as the wire is large enough. I figure each light will draw about 2.17 amps. Ambient temperature derate is .82 and I calculated the voltage drop at a little over 5%. I was going to run a #10 awg ground with this. The distance between lights is 30 feet with the 1000 foot mark being the last light. I am running two separate two wire 380 volt circuits and hitting every other light.
So at each of the Tees on the main run I was wanting to splice #12s to go from the main run to the fixture.
So if my home run is #6, The breaker for this circuit is 40 amps, then I could tap off the homerun with #12 wire to feed each fixture as long as it is not over 6 feet in length?
Thanks for the quick replies. This 1000 ft run is to the further most lights. I will have 10 175 watt 380 volt Metal Halide wall packs on the run. Site voltage is 220/380 volt 50 hz and the breaker will be a 2 pole 40. Don't really need this large a breaker but the shorter runs have more lights on the circuit so I was just keeping the breaker size the same as the wire is large enough. I figure each light will draw about 2.17 amps. Ambient temperature derate is .82 and I calculated the voltage drop at a little over 5%. I was going to run a #10 awg ground with this. The distance between lights is 30 feet with the 1000 foot mark being the last light. I am running two separate two wire 380 volt circuits and hitting every other light.
So at each of the Tees on the main run I was wanting to splice #12s to go from the main run to the fixture.