I have a question regarding 240.21(B)(1)
If a feeder is suitably protected and tapped to supply multiple panelboards. Is it acceptable for the panelboards to be MLO if the taps are the same size as the feeder?
Common sense tells me that the taps are still protected by the OCPD at the feeder from both overload and short circuits. They cannot be overloaded due to the feeder OCPD being at a lower current rating than the ampacity of the cable. For shorts circuits, a breaker at the termination wouldn't provide protection anyways it wouldn't see a fault on the cable.
However, per 240.21(B)(1)(b) they appear they must terminate into a OCPD.
Is there some exception that makes taps not considered taps if they are equal or greater than their feeder?
For what it's worth this is a current installation and I am trying to see if it is code compliant or not.
Thanks!
If a feeder is suitably protected and tapped to supply multiple panelboards. Is it acceptable for the panelboards to be MLO if the taps are the same size as the feeder?
Common sense tells me that the taps are still protected by the OCPD at the feeder from both overload and short circuits. They cannot be overloaded due to the feeder OCPD being at a lower current rating than the ampacity of the cable. For shorts circuits, a breaker at the termination wouldn't provide protection anyways it wouldn't see a fault on the cable.
However, per 240.21(B)(1)(b) they appear they must terminate into a OCPD.
Is there some exception that makes taps not considered taps if they are equal or greater than their feeder?
For what it's worth this is a current installation and I am trying to see if it is code compliant or not.
Thanks!